How do you have this wired? Not sure these two systems can work together. wind unit looks like a 12 or 24 volt system and the other is a 48 volt system
How do you have this wired? Not sure these two systems can work together. wind unit looks like a 12 or 24 volt system and the other is a 48 volt system
@Carlo Monaghan what size wire do you have from your battery to your inverter? How many lights do you have and their wattage? You only have 600 watts to play with. Should be running led to g...
4 100 ah batteries is a lot of storage. Should work flawlessly how much load do you have on your system? 10240 watt hours is what I run on my 3000 watt ecoworthy all in one and I have 1000 watts of...
@Tom Stager do you have a shunt inline to measure the wattage going into and out of you batteries? Your batteries may not be fully charged enough to make it through the night. If you have an ...
@Robert Thomas I would connect two in series then those two in parallel just to drop the amps in the wire to the controller. Lots of things to consider will any panels get shaded through out the da...
I charge batteries like this all the time. The bms should take care of the batteries for you. If one charges fast that the other the bms will shut it off and continue to charge the other.
Sounds like a charging problem. How are you charging them?
Are you running them series or parallel or combined? I would series the panels to get as much voltage as the solar generator will allow. This will lower your amperage. Remember you can not allow th...
@Sam Carpenter I bulk charge at 29.2 and float at 26.8. battery and utility are subject to how much you want to drain your battery. I switch to utilities at 26 volts and back to battery...
You have your 01 setting at sol and as you loose sunlight it will cycle off and on as the as it drops below and above the pv voltage threshold. I installed a pv contactor with a clock function to j...
Your connections don't look tight. Also make sure the wire lugs mate together properly. Check how the lug sits on the battery terminal it must be flat contacting the entire surface. Positive parall...
If you have any questions just ask I don't get on this site often but I do like experimenting with different settings and trying to get the most out of my small solar system. And for the pr...
Before I had free electricity after 8 I ran mine like this and let it bypass at night and turned the mains charging to 0 I think it parameter 28. I really wish these parameters could be changed on ...
If you run 1 on sol and 6 on cso this is the other way I run my system and I turn on Mains power at 8pm to recharge. If you have mains power turned on as soon as you lose solar it will switch to by...
This is how I run mine. But my electric contract is for free power after 8 pm.
To get it to use solar you have to run on sol and when you loose solar it switches to mains charging.
It does have a delay. I think mine is about 5 minutes. I can't seem to get the time stamp to sink up either. I'm off by an hour. I monitor two units with the app. It's pretty basic but I just want ...
When you get battery low enough to trip 04 it will go to bypass. When solar charges it up to 05 it will switch back to battery.
You will need a split phase inverter for 240v because the phases from two different inverters won't stay in phase. I would look at one of the hybrid packages and ask tech support to make sure it wi...
parameter 1 should be SBU parameter 6 should be OSO This is how i set mine up most of the time. Yous have to adjust P04 and P05 for the voltage you want the system to go to utility on and back t...